GFCI stands for Ground Fault Circuit Interrupter, and it means the outlet that can prevent electrical shock in wet locations such as bathrooms, kitchens and outdoor areas. Depending on local zoning it is most likely necessary for resale and possibly also required if you are remodeling. It may not be necessary but it is wise as an ounce of prevention is worth a pound of cure.
Based on 2014 NEC Code:
210.8(A)(7) GFCI PROTECTION FOR PERSONNEL DWELLING UNITS.
Any 125 V, single-phase,15- or 20- amp receptacle within 6 ft. of the outside edge of a sink in a dwelling unit must now have ground-fault circuit-interrupter (GFCI) protection. This requirement is now for kitchens as well as other areas of the dwelling unit. This includes receptacles for a garbage disposal, refrigerator, or range hood, if they are within 6 ft. of the sink. The distance does not have to be horizontal, so a receptacle on a kitchen island would require GFCI protection if the shortest route to the sink was less than 6 ft.
A GFCI should be installed per the National Electrical Code requirements and yes it is necessary. The GFCI is installed for the safety of the home owner and should be installed in bathrooms, kitchens, outdoors, garages, unfinished basements, crawl spaces, jetted tubs, hot tubs, water fountains and pools. The GFCI will trip instantly if it senses a ground fault and could possibly save your life.
Absolutely necessary.
Absolutely
It’s definitely a good idea. GFCI outlets a code required for new construction and are a safer alternative to a regular outlet.
Yes, per all the other professionals that answered this question prior to us.
Simple Answer Yes This Is Very Important, And Required By Code… If It is within 6 ft ,
Yes! For two reasons.
#1: It can save your life!
#2: The NEC requires it.
This is a definite must.
Your contractor is 100% correct and it is required by code to install a GFCI.